Sounds like a good enough reason for a GFCI at
every isolated outlet.

Although I'm now wondering if the
real answer isn't RCBO:- "Residual-current Circuit Breaker with Overcurrent protection"*. I'm not sure if these are available for single circuits (individual outlets), however.
MCB Types:-
Type B are designed to trip at fault currents of 3 to 5 times rated current (In).
For example a 10 A device will trip at 30 to 50 A.
Type C are designed to trip at 5 to 10 times In (50 to 100 A for a 10 A device).
Type D are designed to trip at 10 to 20 times In (100 to 200 A for a 10 A device).
I wonder what became of Type A?1)
Source2) Many
others are available.
*
An RCBO is a combination of an MCB and RCD and provides both overcurrent protection and earth fault current protection in a a single device.