Sounds like a good enough reason for a GFCI at every isolated outlet. smile

Although I'm now wondering if the real answer isn't RCBO:- "Residual-current Circuit Breaker with Overcurrent protection"*. I'm not sure if these are available for single circuits (individual outlets), however.

Originally Posted By: Mr.Google

MCB Types:-

Type B are designed to trip at fault currents of 3 to 5 times rated current (In).
For example a 10 A device will trip at 30 to 50 A.

Type C are designed to trip at 5 to 10 times In (50 to 100 A for a 10 A device).

Type D are designed to trip at 10 to 20 times In (100 to 200 A for a 10 A device).


I wonder what became of Type A?

1) Source

2) Many others are available.

* An RCBO is a combination of an MCB and RCD and provides both overcurrent protection and earth fault current protection in a a single device.